BadFilterNotAllowed OPC-UA error with KepserverEX V6
31 May 2017 17:13 #5188 by support
At a first glance, I do not see anything wrong with your code; this is reinforced by the fact that it has worked with previous server version.
I suggest to wait for a reply from Kepware, because it is quite likely there is an issue on their side, or that at least they can hint to a possible cause.
31 May 2017 16:05 #5186 by sun21
Problem:
After we've upgraded KepserverEx OPC server from V5 to V6 errors appeared.
Client subscription to tags with boolean datatype are failing with following message.
(everything was OK for KS V5 --> OPC client v4.51, our C# code was not changed.)
Message:
..., error code: -2142961664, error message: OPC-UA service result - An error specific to OPC-UA service occurred.
---- SERVICE RESULT ----
StatusCode: {BadFilterNotAllowed} = 0x80450000 (2152005632)
Event handler code:
private void MonitoredItemChangedEvent(object self, EasyUADataChangeNotificationEventArgs e) { var tag = e.Arguments.NodeDescriptor.NodeId.Identifier.ToString(); if (e.Succeeded && e.Exception == null) { ... } else { Logger.LogError(string.Format("Failed to write item changed event for tag '{2}', error code: {0}, error message: {1}. (repeated messages will be suppressed)", e.ErrorCode, e.ErrorMessage, tag)); }
Subscription code:
... filter = new UADataChangeFilter(UADataChangeTrigger.StatusValue); easyUaMonitoredItemArguments.Add( new EasyUAMonitoredItemArguments(MonitoredItemChangedEvent, dataItemHandle, _endPointDescriptor, nodeDescriptor, new UAMonitoringParameters(dataItem.SamplingIntervalMs, filter, _uaMonitoringQueueSize ) ) ); var monitoredItemHandles = _easyUaClient.SubscribeMultipleMonitoredItems(easyUaMonitoredItemArguments.ToArray()); ...
We are not sure where to look.
Can you please suggest a solution or workaround? KS support was also notified.